I do not use previously used oil in the hammer. I do use cheap oil and plenty of it. I use good quality grease for the bearings. I recycle the oil after it has been used in the hammer in my alaska mill auxiliary oiler. The bar is 5 feet long and is sometimes cutting through 4+ feet of eastern hardwood which can be difficult for the chainsaw's integral oiler to keep well lubricated. I am certainly not endorsing doing anything the way I do it.
So, this nuisance tripping I have been tracking... Steve is right, had the splice box been sealed properly those mice would not have caused a problem but I overlooked one spot. That is done now but the nuisance tripping at about the 15-20 minute mark persisted.
I will have a chance to run the hammer full out again tomorrow. If it happens again I will find an "amp clamp" to meter amp draw. Should I also consider replacing the 100A breaker at the service panel?
Thanks to all for weighing in
-
I suppose running dry and cold could be a possible problem. I have run it just as it is for years without issue, though. I usually prime it and let it warm up at an idle while the coal forge is waking up.
What oil do you run through yours? I have been using chainsaw bar oil that gets reused on the aux oiler on my alaska mill. Been doing that for a decade at least.
I have inspected all splice points but the buried one and tightened things up. I am going to run things today in hopes it is just that simple. If it pops again I will pick up an amp clamp.
-
The sub panel is 100A. Other loads would be coal forge blower, a half dozen florescent shop lights, a box fan on low aimed at the wood stove.
I checked the only other accessible splice before the subpanel and it appeared to be fine. It was a while ago I put it in so I dont remember if I used antiox on the aluminum but it is something I generally do, working it in a little with a wire brush.
I suppose I will check ahead of the sub panel now. I did all this wiring myself including trenching the 200 rocky feet to the shop. A rookie mistake is a possibility.
Any recommendations on an Amp meter? Is this the same as a multimeter? I believe I know where to borrow one of those...
Also, should trying a new breaker be considered?
Thanks again
-
I have a problem.
I am forging down 1" square stock with the #88 striker air hammer, 5HP, 1ph converted to 3ph through a VFD and the 100A breaker at the main service panel trips after about 20 minutes of work. Shop subpanel does not trip. I opened up the splice box between the service panel and the shop subpanel and found a mouse family and damaged ground and neutral. Fixed that and went back to work. Happened again.
I have two other splice points between the shop and the main service panel. One where the wire dives underground and one halfway to the shop underground. 2/0 Aluminum, rated for direct burial, some in plastic conduit, some not.
I live in way northern New York state. Things are just freezing up.
Any ideas? Any tricks for diagnosing/measuring to suggest?
Thanks in advance.....
-
-
Just tried the burner out in an old forge shell. Extremely stable flame at least for the 15 minutes of run time my near dead empty 20 pounder afforded. I will go pull the spare off the camper later and post pictures or a short video.
Flame was a little reducing which I suppose could be addressed by modifying the reil type burner's air intake size.
The flame was perfectly stable and very quiet over a wide range as well.
I wish I had the time to change out my production slot forge from blown to n.a.
Thanks again for sharing your discoveries.
-
-
Hi Dan. First time on ifi in a long time. So I just converted my home built slot forge to blown ribbon and now I'm looking to change over my portable. It currently uses a single zoeller type propane 3/4" n.a. burner. In your opinion would this burner convert to run a ribbon head?
Any electricians in the house?
in Power Hammers, Treadle Hammers, Olivers
Posted
Problem solved. The nuisance tripping has stopped. Repairing the rodent damage and cleaning/tightening all connections seems to have done the trick. I have been running the hammer for hours the past few days, mig welding, plasma, big compressor, etc.
Thanks to all for the input.