This is not a you or me thing, its the US national electrical code (NEC), and as your address as posted is in the states, it applies, no matter what degree you may have. If it is not according to the NEC then it is "not to code", as that is what wired to code means.

I was trying to prevent a person from following your advice as to wire gauge. I know that the code is not easy to understand, that is why I said avoid amature electricians. NEC section 240.4 sub D is clear about 12 gauge wire and max amperage allowed as 20 amps. NO exceptions, and I did post that 310.16 is for calculation the voltage drop only. it IS NOT a chart for breaker sizes. I was correcting your misstatement of "...#12 can carry 25 amps.." and that is false. Under ANY condition.

I stand by what I said, #12 must NEVER be fused above 20 amps. period. I am sorry you took this as a personal attack,

If you looked at the chart in question you would see the asterisk beside the gauge size, that asterisk calls attention to read what is known as a fine print note. the NEC is full of them, and a qualified Electrician should know. Most amatures do not,. Maybe you have a different definition of amature than I do.

I do electrical work for a living. Florida block, and the California block License exams test the skill of looking up the codes rules and conditions and exceptions. the Exam is a pain to pass. many/most fail the first time.